Question 2085 of 172 · Texas Fire Alarm License Exam
Fire alarm system batteries must be marked with
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2085
- D: the month and year of manufacture
Explanation
Batteries must be marked with the month and year of manufacture so their age can be tracked for maintenance and replacement.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2086Primary power for a protected premises fire alarm system is generally supplied by
- 2087The location of the fire alarm branch circuit disconnecting means must be
- 2088A listed relay or control module used for an emergency control function must be located within what distance of the controlled component?
- 2089After acceptance of a new system, the document that summarizes the system and its testing is the
- 2001For a protected premises fire alarm system, NFPA 72 requires secondary power capable of operating the system in quiescent load for
- 2002A fire alarm panel draws 0.45 A in standby and 2.8 A in alarm. Using 24 hours standby, 5 minutes alarm and the 20 percent safety margin required by NFPA 72 (2019), the minimum battery is about