Question 2088 of 172 · Texas Fire Alarm License Exam
A listed relay or control module used for an emergency control function must be located within what distance of the controlled component?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2088
- C: 3 feet
Explanation
The relay or module for emergency control functions must be within 3 ft of the component it controls, so the wiring between them is short and protected.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2089After acceptance of a new system, the document that summarizes the system and its testing is the
- 2001For a protected premises fire alarm system, NFPA 72 requires secondary power capable of operating the system in quiescent load for
- 2002A fire alarm panel draws 0.45 A in standby and 2.8 A in alarm. Using 24 hours standby, 5 minutes alarm and the 20 percent safety margin required by NFPA 72 (2019), the minimum battery is about
- 2003An emergency voice/alarm communications system requires secondary power for 24 hours standby followed by how many minutes of alarm at maximum connected load?
- 2004A notification appliance circuit carries 1.5 A to the last appliance 400 ft from the panel on 14 AWG solid copper (about 3.07 ohms per 1,000 ft). The approximate voltage drop is
- 2005A 24 VDC initiating device circuit ends in a 4,700 ohm end-of-line resistor. The supervisory current through the resistor is about