Question 1028 of 344 · NICET Fire Alarm Systems Level II
Cable ties used to secure fire alarm cables in a plenum space must have what property?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1028
- A: Listed for low smoke and heat release
Explanation
In other spaces used for environmental air, nonmetallic cable ties and similar accessories must be listed for low smoke and heat release, so they do not add smoke to the air handling system.
More questions: Installation
- 1029What is the minimum conductor size permitted for NPLFA circuits?
- 1030What is the maximum overcurrent protection for 18 AWG NPLFA conductors?
- 1031What is the minimum insulation voltage rating for NPLFA conductors?
- 1032Which equipment marking does NFPA 70 require where a power supply provides PLFA circuits?
- 1033A contractor wants to run PLFA cable in an elevator hoistway. What does NFPA 70 require?
- 1034What NEC rule governs fire alarm cable penetrations through fire resistance rated walls?