Question 1030 of 344 · NICET Fire Alarm Systems Level II
What is the maximum overcurrent protection for 18 AWG NPLFA conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1030
- D: 7 A
Explanation
NFPA 70 limits overcurrent protection to 7 A for 18 AWG and 10 A for 16 AWG NPLFA conductors. Larger conductors are protected according to their ampacity.
More questions: Installation
- 1031What is the minimum insulation voltage rating for NPLFA conductors?
- 1032Which equipment marking does NFPA 70 require where a power supply provides PLFA circuits?
- 1033A contractor wants to run PLFA cable in an elevator hoistway. What does NFPA 70 require?
- 1034What NEC rule governs fire alarm cable penetrations through fire resistance rated walls?
- 1035Which NFPA 70 article primarily covers fire alarm system wiring?
- 1036PLFA conductors and NPLFA conductors must terminate in the same control unit enclosure. What does NFPA 70 require?