What is the minimum conductor size permitted for NPLFA circuits?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1029
- A: 18 AWG
Explanation
NPLFA conductors of 18 AWG and 16 AWG are permitted when installed within their ampacity, and larger sizes follow the general ampacity tables. 26 AWG is the minimum for conductors in multiconductor PLFA cable.