Question 1047 of 344 · NICET Fire Alarm Systems Level II
For elevator shunt trip, how close must the heat detector be to each sprinkler head it protects?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1047
- C: Within 2 ft
Explanation
Heat detectors used for elevator power shutdown must be within 24 in. (610 mm) of each sprinkler head and have a lower temperature rating and higher sensitivity than the sprinkler.