Question 1047 of 344 · NICET Fire Alarm Systems Level II

For elevator shunt trip, how close must the heat detector be to each sprinkler head it protects?

Exactly one answer is correct.

Show solution

Correct answer to question 1047

  • C: Within 2 ft

Explanation

Heat detectors used for elevator power shutdown must be within 24 in. (610 mm) of each sprinkler head and have a lower temperature rating and higher sensitivity than the sprinkler.

Next to question ›