Question 1048 of 344 · NICET Fire Alarm Systems Level II

Which signal should a sprinkler waterflow switch with retard delay produce, and what is the maximum delay allowed before the alarm is initiated?

Exactly one answer is correct.

Show solution

Correct answer to question 1048

  • B: An alarm signal within 90 seconds of sustained flow

Explanation

Waterflow alarm initiating devices must produce an alarm signal within 90 seconds of a flow equal to or greater than a single sprinkler of the smallest orifice. Retard settings are adjusted to avoid surges but stay within that limit.

Next to question ›