What is the nominal spacing for spot-type smoke detectors on a smooth ceiling when no other spacing is specified?

Exactly one answer is correct.

Show solution

Correct answer to question 1049

  • C: 30 ft

Explanation

Spot-type smoke detectors on smooth ceilings use a nominal spacing of 30 ft (9.1 m). All points on the ceiling must be within 0.7 times the selected spacing of a detector.