A spot smoke detector is to be mounted on a sidewall instead of the ceiling. Where must its top edge be?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1052
- A: Between 4 in. and 12 in. below the ceiling
Explanation
Sidewall mounted spot smoke detectors must have the top of the detector between 4 in. and 12 in. (100 mm and 300 mm) below the ceiling. Ceiling mounted detectors may be placed anywhere on the ceiling, including close to the wall.
More questions: Installation
- 1053What minimum distance should a spot smoke detector be from a forced air supply diffuser?
- 1054On a peaked ceiling, where must the first row of smoke detectors be installed?
- 1055How is spacing determined for spot-type heat detectors?
- 1056A heat detector listed for 50 ft spacing will be installed on a smooth ceiling 15 ft high. The reduction factor for a ceiling height above 14 ft up to 16 ft is 0.77. What is the adjusted spacing?
- 1057A heat detector with a listed spacing of 30 ft will be installed on a 12.5 ft high ceiling. The multiplier above 12 ft up to 14 ft is 0.84. What spacing must be used?