Question 1046 of 344 · NICET Fire Alarm Systems Level II
Which kind of detector is normally used to initiate elevator power shutdown (shunt trip) before sprinklers discharge in the machine room?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1046
- C: A heat detector rated lower and more sensitive than the sprinkler
Explanation
Shunt trip is initiated by heat detectors located within 24 in. of each sprinkler, rated lower and more sensitive than the sprinkler, so power is removed before water is discharged on the equipment.
More questions: Installation
- 1047For elevator shunt trip, how close must the heat detector be to each sprinkler head it protects?
- 1048Which signal should a sprinkler waterflow switch with retard delay produce, and what is the maximum delay allowed before the alarm is initiated?
- 1049What is the nominal spacing for spot-type smoke detectors on a smooth ceiling when no other spacing is specified?
- 1050Using the 0.7S rule with a 30 ft nominal spacing, every point on a smooth ceiling must be within what distance of a smoke detector?
- 1051With smooth ceiling spacing of 30 ft, what is the maximum distance from a wall to the nearest row of spot smoke detectors?
- 1052A spot smoke detector is to be mounted on a sidewall instead of the ceiling. Where must its top edge be?