On a peaked ceiling, where must the first row of smoke detectors be installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1054
- D: Within 3 ft of the peak, measured horizontally
Explanation
For peaked ceilings, a row of detectors is placed within 3 ft (0.9 m) of the peak measured horizontally. Additional detectors are spaced based on the horizontal projection of the ceiling.
More questions: Installation
- 1055How is spacing determined for spot-type heat detectors?
- 1056A heat detector listed for 50 ft spacing will be installed on a smooth ceiling 15 ft high. The reduction factor for a ceiling height above 14 ft up to 16 ft is 0.77. What is the adjusted spacing?
- 1057A heat detector with a listed spacing of 30 ft will be installed on a 12.5 ft high ceiling. The multiplier above 12 ft up to 14 ft is 0.84. What spacing must be used?
- 1058Where should a sidewall mounted spot heat detector be located?
- 1059On a ceiling with solid joists, how is heat detector spacing adjusted in the direction perpendicular to the joists?
- 1060What governs the spacing and mounting of projected beam smoke detectors?