Question 1055 of 344 · NICET Fire Alarm Systems Level II
How is spacing determined for spot-type heat detectors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1055
- A: By listed spacing, reduced for ceiling height or construction
Explanation
Heat detectors are installed at their listed spacing, which comes from fire tests. That spacing is reduced for ceiling height above 10 ft and for beam or joist construction.
More questions: Installation
- 1056A heat detector listed for 50 ft spacing will be installed on a smooth ceiling 15 ft high. The reduction factor for a ceiling height above 14 ft up to 16 ft is 0.77. What is the adjusted spacing?
- 1057A heat detector with a listed spacing of 30 ft will be installed on a 12.5 ft high ceiling. The multiplier above 12 ft up to 14 ft is 0.84. What spacing must be used?
- 1058Where should a sidewall mounted spot heat detector be located?
- 1059On a ceiling with solid joists, how is heat detector spacing adjusted in the direction perpendicular to the joists?
- 1060What governs the spacing and mounting of projected beam smoke detectors?
- 1061Why must projected beam smoke detectors be mounted on stable surfaces?