Question 1081 of 344 · NICET Fire Alarm Systems Level II
What is the maximum sound pressure level a fire alarm audible signal may produce?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1081
- B: 110 dBA at the minimum hearing distance
Explanation
The total sound pressure level produced by the combination of ambient and alarm signals must not exceed 110 dBA at the minimum hearing distance, to limit the risk of hearing damage.
More questions: Installation
- 1082What is the purpose of system commissioning before the acceptance test?
- 1083During an initial acceptance test, which devices must be tested?
- 1084Before connecting field wiring to the control unit, which test checks for unintended grounds and stray voltage on new circuits?
- 1085What instrument is used to measure insulation resistance of new fire alarm conductors to ground?
- 1086Where must spot smoke detectors be installed relative to a ceiling fan blade?
- 1087A smoke detector is planned in a room where the ambient temperature can reach 120 F. What must the technician verify?