A 40 ft by 40 ft room will be covered by one wall mounted strobe. What minimum effective intensity does the wall mounted room table require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1100
- D: 60 cd
Explanation
The wall mounted room table requires 60 cd for one appliance in a 40 ft by 40 ft room. Using two appliances on opposite walls lowers the required intensity per appliance.
More questions: Installation
- 1101Which control function is commonly wired from a fire alarm relay to release magnetically held smoke doors?
- 1102Where must the relay or control module that operates an emergency control function be located?
- 1103How are HVAC fan shutdown circuits typically installed when they are not monitored for integrity?
- 1104What must happen to the fire alarm system when an emergency control function interface relay fails?
- 1105Which interface must be provided so that elevators are not recalled to a floor where the lobby detector is in alarm?
- 1106What should a technician do before connecting the fire alarm system to the supervising station during installation?