Question 1115 of 344 · NICET Fire Alarm Systems Level II
Which mounting rule applies when a detector is installed in an air sampling or pipe network for aspirating smoke detection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1115
- C: Each port is treated as a spot detector for spacing
Explanation
Each sampling port of an air sampling system is considered equivalent to a spot type detector for spacing. Transport time from the farthest port must also be verified, usually within 120 seconds.
More questions: Installation
- 1116What is the maximum transport time from the most remote sampling port of an air sampling detector to the detector?
- 1117Before starting rough-in, what should the technician confirm about the building's sprinkler system for a waterflow interface?
- 1118What is the maximum height above the floor for the highest operable switch or indicator on a fire alarm control unit display, unless the AHJ approves otherwise?
- 1119What is the minimum height above the floor for the lowest switch or bottom of the text display on a fire alarm control unit?
- 1120Which device type must be installed in an elevator hoistway that has sprinklers at the top, to support elevator recall?
- 1001Which pathway class includes a redundant path and keeps operating past a single open, but is not required to keep operating past a single short?