Before starting rough-in, what should the technician confirm about the building's sprinkler system for a waterflow interface?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1117
- D: The waterflow, tamper, and other supervisory points
Explanation
The fire alarm installer needs to know each waterflow switch, valve tamper switch, and other supervisory device (low air, low temperature, pump signals) so circuits and modules are planned correctly.