What is the maximum transport time from the most remote sampling port of an air sampling detector to the detector?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1116
- A: 120 seconds
Explanation
Air sampling systems must be designed so that the transport time from the farthest port does not exceed 120 seconds, and this is verified at acceptance and during periodic testing.