Which device type must be installed in an elevator hoistway that has sprinklers at the top, to support elevator recall?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1120
- A: A smoke detector at the top of the hoistway
Explanation
Where sprinklers are installed in the hoistway, smoke detection is generally required at the top of the hoistway to initiate recall, with the activation sending cars to the designated level.
More questions: Installation
- 1001Which pathway class includes a redundant path and keeps operating past a single open, but is not required to keep operating past a single short?
- 1002A technician opens one conductor in the middle of a Class B initiating device circuit. What happens to the devices beyond the break?
- 1003Which pathway class is designed to keep operating during a single short circuit on the pathway?
- 1004A door holder circuit releases the doors whenever its pathway fails, and no trouble is annunciated. Which pathway class describes this behavior?
- 1005Which pathway class applies to pathways that are not monitored for integrity at all?
- 1006An IP based link to a remote annunciator is checked only through periodic end to end communication, and loss of that communication is reported as trouble. The individual paths are not monitored. Which class is this?