Question 1118 of 344 · NICET Fire Alarm Systems Level II
What is the maximum height above the floor for the highest operable switch or indicator on a fire alarm control unit display, unless the AHJ approves otherwise?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1118
- D: 6 ft
Explanation
Control unit displays, visible indicators, and controls must be mounted so the highest switch, lamp, or top of text display is not more than 6 ft (1.8 m) above the floor, and the lowest is not within 15 in. of the floor.
More questions: Installation
- 1119What is the minimum height above the floor for the lowest switch or bottom of the text display on a fire alarm control unit?
- 1120Which device type must be installed in an elevator hoistway that has sprinklers at the top, to support elevator recall?
- 1001Which pathway class includes a redundant path and keeps operating past a single open, but is not required to keep operating past a single short?
- 1002A technician opens one conductor in the middle of a Class B initiating device circuit. What happens to the devices beyond the break?
- 1003Which pathway class is designed to keep operating during a single short circuit on the pathway?
- 1004A door holder circuit releases the doors whenever its pathway fails, and no trouble is annunciated. Which pathway class describes this behavior?