A door holder circuit releases the doors whenever its pathway fails, and no trouble is annunciated. Which pathway class describes this behavior?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1004
- A: Class D
Explanation
Class D pathways have fail safe operation: when the pathway fails, the intended action (here, releasing the door) is performed, and fault annunciation is not required. Class E is simply not monitored for integrity.