Which pathway class is designed to keep operating during a single short circuit on the pathway?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1003
- A: Class X
Explanation
Class X performs like Class A and additionally continues to operate past a single short and past an open combined with a ground fault, usually by means of short circuit isolators. Class A only has to survive a single open.
More questions: Installation