Which pathway class applies to pathways that are not monitored for integrity at all?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1005
- C: Class E
Explanation
Class E describes pathways that are not monitored for integrity, such as some circuits within a single enclosure or to nonrequired equipment. Class D is fail safe, and Class C relies on end to end verification.