A technician opens one conductor in the middle of a Class B initiating device circuit. What happens to the devices beyond the break?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1002
- D: They stop reporting, and the panel shows trouble
Explanation
A Class B pathway has no redundant path, so operational capability stops at the open. The supervision current through the end of line device is interrupted, which the control unit annunciates as trouble, not alarm.