A technician opens one conductor in the middle of a Class B initiating device circuit. What happens to the devices beyond the break?

Exactly one answer is correct.

Show solution

Correct answer to question 1002

  • D: They stop reporting, and the panel shows trouble

Explanation

A Class B pathway has no redundant path, so operational capability stops at the open. The supervision current through the end of line device is interrupted, which the control unit annunciates as trouble, not alarm.