The control unit shows a ground fault trouble. What is the most efficient first step to locate it?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2028
- A: Lift circuits one at a time until the fault clears
Explanation
Isolating circuits one at a time shows which circuit carries the ground. That circuit is then split at junction points (half splitting) until the faulted section is found.
More questions: Maintenance
- 2029A technician measures resistance from one conductor of a disconnected circuit to a known building ground. Which reading suggests a ground fault?
- 2030With field wiring disconnected and the far end of a Class B IDC open (EOL removed), what reading between the two conductors indicates a short?
- 2031A Class B IDC with a 4.7 kilohm EOL resistor reads infinite resistance at the panel terminals with field wiring removed. What does this indicate?
- 2032A 24 VDC NAC with a 2.2 kilohm EOL is checked with the panel in normal (supervisory) condition. Which measurement confirms the EOL is in place?
- 2033Why are notification appliances on a supervised NAC polarized (diode blocked)?
- 2034Using Ohm's law, a circuit draws 0.5 A at 24 V. What is the circuit resistance?