Question 2062 of 344 · NICET Fire Alarm Systems Level II
What is a typical float charge voltage for a 24 V sealed lead acid battery set (two 12 V batteries)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2062
- A: About 27.3 V
Explanation
Sealed lead acid batteries are float charged at roughly 2.25 to 2.3 V per cell. A 24 V set has 12 cells, so about 27 to 27.6 V. Always follow the battery manufacturer's specified voltage.