Question 2064 of 344 · NICET Fire Alarm Systems Level II
What is the typical end voltage used for a 24 V battery set at the end of its required standby and alarm period?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2064
- B: 20.4 V
Explanation
Many manufacturers and calculations use 20.4 V (85 percent of 24 V, or 1.7 V per cell) as the minimum end of discharge voltage for 24 V systems. Notification circuits must work at this lowest voltage.
More questions: Maintenance
- 2065How often must the month and year marking on sealed (VRLA) batteries be checked against the manufacturer replacement date?
- 2066How is a fire alarm audible appliance's sound level checked when the ambient noise in an area has changed since acceptance?
- 2068A technician arrives for an annual test and finds a smoke detector covered with a plastic bag. What should be done?
- 2069Why should alarm verification be checked during periodic testing of smoke detector circuits?
- 2070What is the maximum alarm verification time allowed for smoke detectors under NFPA 72?
- 2071Which testing practice prevents unnecessary fire department response during an annual test?