How often must the month and year marking on sealed (VRLA) batteries be checked against the manufacturer replacement date?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2065
- B: Semiannually
Explanation
Table 14.3.1 has VRLA batteries checked semiannually for the manufacture month and year marking. A battery is replaced once the equipment manufacturer replacement date has passed. The general condition check (leaks, corrosion, loose connections) is done at acceptance.