Question 2063 of 344 · NICET Fire Alarm Systems Level II
During an annual test, the panel is switched from primary to secondary power. What should be verified?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2063
- D: It runs on batteries and transfers back correctly
Explanation
Disconnecting primary power confirms that secondary power takes over, a trouble signal is produced, and the system transfers back when power is restored, with the charger recharging the batteries.
More questions: Maintenance
- 2064What is the typical end voltage used for a 24 V battery set at the end of its required standby and alarm period?
- 2065How often must the month and year marking on sealed (VRLA) batteries be checked against the manufacturer replacement date?
- 2066How is a fire alarm audible appliance's sound level checked when the ambient noise in an area has changed since acceptance?
- 2068A technician arrives for an annual test and finds a smoke detector covered with a plastic bag. What should be done?
- 2069Why should alarm verification be checked during periodic testing of smoke detector circuits?
- 2070What is the maximum alarm verification time allowed for smoke detectors under NFPA 72?