Question 2070 of 344 · NICET Fire Alarm Systems Level II
What is the maximum alarm verification time allowed for smoke detectors under NFPA 72?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2070
- C: 60 seconds
Explanation
Alarm verification may not delay the alarm by more than 60 seconds total, including the retard, reset, and restart periods. Verification is not used on other detector types or waterflow.
More questions: Maintenance
- 2071Which testing practice prevents unnecessary fire department response during an annual test?
- 2072What must be tested on the supervising station transmitter during periodic testing?
- 2073A dual path communicator loses its cellular path but keeps its IP path. What must the system do?
- 2074When replacing a failed addressable smoke detector with a new one, what must the technician verify?
- 2075Which document should be used to confirm the correct operation of each input and output during testing?
- 2076A technician finds several corroded terminals in an outdoor junction box on an IDC. Which fault is most likely to result?