Question 2071 of 344 · NICET Fire Alarm Systems Level II
Which testing practice prevents unnecessary fire department response during an annual test?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2071
- C: Put the account on test and confirm signals arrive
Explanation
The supervising station is told the account is on test so signals are logged but not dispatched. The technician still confirms that each type of signal arrives correctly.
More questions: Maintenance
- 2072What must be tested on the supervising station transmitter during periodic testing?
- 2073A dual path communicator loses its cellular path but keeps its IP path. What must the system do?
- 2074When replacing a failed addressable smoke detector with a new one, what must the technician verify?
- 2075Which document should be used to confirm the correct operation of each input and output during testing?
- 2076A technician finds several corroded terminals in an outdoor junction box on an IDC. Which fault is most likely to result?
- 2077An SLC with 60 addressable devices has a ground fault. The technician lifts the field wiring at device 30 and the ground fault trouble clears. Where is the fault?