Question 2077 of 344 · NICET Fire Alarm Systems Level II

An SLC with 60 addressable devices has a ground fault. The technician lifts the field wiring at device 30 and the ground fault trouble clears. Where is the fault?

Exactly one answer is correct.

Show solution

Correct answer to question 2077

  • D: Between device 30 and the end of the loop

Explanation

Lifting the wiring at device 30 disconnects everything beyond it. Because the fault cleared, the grounded conductor is in the far half. The technician repeats the split in that half (half splitting) to narrow it down.