Question 2077 of 344 · NICET Fire Alarm Systems Level II
An SLC with 60 addressable devices has a ground fault. The technician lifts the field wiring at device 30 and the ground fault trouble clears. Where is the fault?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2077
- D: Between device 30 and the end of the loop
Explanation
Lifting the wiring at device 30 disconnects everything beyond it. Because the fault cleared, the grounded conductor is in the far half. The technician repeats the split in that half (half splitting) to narrow it down.
More questions: Maintenance
- 2078A ground fault trouble appears only during heavy rain and clears in dry weather. What is the most likely cause?
- 2079A Class A IDC shows an open circuit trouble, yet every device on it still alarms when tested. Why?
- 2080A short circuit occurs on a Class A SLC that has isolator modules between groups of devices. What is the expected result?
- 2081A NAC has 12 strobes. The technician removes the EOL resistor and measures resistance across the disconnected field conductors with the meter leads in normal polarity. The reading is a few ohms. What does it indicate?
- 2082During an annual test, a horn strobe works on AC power but fails to operate after the panel transfers to batteries. Which is the most likely cause?
- 2083A technician measures 20.8 V at the last appliance in alarm with the panel on batteries. The appliances are listed for 16 V to 33 V. What is the conclusion?