Question 2079 of 344 · NICET Fire Alarm Systems Level II

A Class A IDC shows an open circuit trouble, yet every device on it still alarms when tested. Why?

Exactly one answer is correct.

Show solution

Correct answer to question 2079

  • B: The panel feeds the circuit from both ends

Explanation

A Class A pathway returns to the control unit, so a single open still leaves every device connected from one direction or the other. The trouble must still be found and repaired, because a second fault could disable devices.