Question 2079 of 344 · NICET Fire Alarm Systems Level II
A Class A IDC shows an open circuit trouble, yet every device on it still alarms when tested. Why?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2079
- B: The panel feeds the circuit from both ends
Explanation
A Class A pathway returns to the control unit, so a single open still leaves every device connected from one direction or the other. The trouble must still be found and repaired, because a second fault could disable devices.
More questions: Maintenance
- 2080A short circuit occurs on a Class A SLC that has isolator modules between groups of devices. What is the expected result?
- 2081A NAC has 12 strobes. The technician removes the EOL resistor and measures resistance across the disconnected field conductors with the meter leads in normal polarity. The reading is a few ohms. What does it indicate?
- 2082During an annual test, a horn strobe works on AC power but fails to operate after the panel transfers to batteries. Which is the most likely cause?
- 2083A technician measures 20.8 V at the last appliance in alarm with the panel on batteries. The appliances are listed for 16 V to 33 V. What is the conclusion?
- 2084A strobe NAC draws 2.4 A in alarm. The run is 250 ft one way of 12 AWG solid copper (1.93 ohms per 1000 ft). What is the voltage drop, treating the load at the end?
- 2085An owner asks to add 6 strobes drawing 0.15 A each to an existing NAC that already draws 1.7 A. The NAC is rated 2.5 A. What is the new load?