Question 2078 of 344 · NICET Fire Alarm Systems Level II
A ground fault trouble appears only during heavy rain and clears in dry weather. What is the most likely cause?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2078
- A: Water entering an outdoor or underground box
Explanation
Intermittent grounds that follow the weather usually come from moisture in exterior junction boxes, underground conduit, or devices on outside walls. These locations should be inspected and sealed or rewired with suitable wiring methods.
More questions: Maintenance
- 2079A Class A IDC shows an open circuit trouble, yet every device on it still alarms when tested. Why?
- 2080A short circuit occurs on a Class A SLC that has isolator modules between groups of devices. What is the expected result?
- 2081A NAC has 12 strobes. The technician removes the EOL resistor and measures resistance across the disconnected field conductors with the meter leads in normal polarity. The reading is a few ohms. What does it indicate?
- 2082During an annual test, a horn strobe works on AC power but fails to operate after the panel transfers to batteries. Which is the most likely cause?
- 2083A technician measures 20.8 V at the last appliance in alarm with the panel on batteries. The appliances are listed for 16 V to 33 V. What is the conclusion?
- 2084A strobe NAC draws 2.4 A in alarm. The run is 250 ft one way of 12 AWG solid copper (1.93 ohms per 1000 ft). What is the voltage drop, treating the load at the end?