How often must door release, fan shutdown, and other emergency control functions be tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2093
- C: Annually
Explanation
Emergency control functions operated by the fire alarm system are tested annually to confirm they operate when the related initiating device activates.