During an annual test, a duct smoke detector alarms but the air handler keeps running. Which item should be checked first?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2094
- D: The shutdown relay and its wiring to the fan control
Explanation
The detector did its job, so the fault is in the output path. The technician checks the control relay, its programming, and the wiring to the fan starter or building automation interface.