Question 2094 of 344 · NICET Fire Alarm Systems Level II

During an annual test, a duct smoke detector alarms but the air handler keeps running. Which item should be checked first?

Exactly one answer is correct.

Show solution

Correct answer to question 2094

  • D: The shutdown relay and its wiring to the fan control

Explanation

The detector did its job, so the fault is in the output path. The technician checks the control relay, its programming, and the wiring to the fan starter or building automation interface.

Next to question ›