Which ceiling condition found during a site survey changes smoke detector spacing?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3008
- D: Beams deeper than 10 percent of ceiling height
Explanation
Beam and joist construction affects how smoke spreads. Deep beams (more than 10 percent of the ceiling height) and beam pockets require adjusted spacing or detectors in each pocket.
More questions: Submittal Preparation and System Layout
- 3009A smooth ceiling room is 60 ft by 90 ft. Detectors are laid out on a 30 ft grid. How many spot smoke detectors are needed?
- 3010A corridor is 10 ft wide. Using the 0.7S rule with S = 30 ft (every point within 21 ft of a detector), what is the maximum spacing between detectors along the centerline?
- 3011A heat detector listed for 50 ft spacing is planned for a 20 ft ceiling. The multiplier for 20 ft is 0.64. What spacing applies?
- 3012A room is 40 ft by 64 ft with a 20 ft smooth ceiling. Heat detectors are listed for 50 ft (adjusted spacing 32 ft). What is the minimum detector count on a square grid?
- 3013A projected beam detector is listed for a maximum beam length of 330 ft and a width of 60 ft. How far from the side wall may the beam be placed?
- 3014A 20 ft by 30 ft room has a 10 ft ceiling and will use one wall mounted strobe in the middle of the long wall. Which room size must be used to pick the candela?