A smooth ceiling room is 60 ft by 90 ft. Detectors are laid out on a 30 ft grid. How many spot smoke detectors are needed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3009
- C: 6
Explanation
60 / 30 = 2 rows and 90 / 30 = 3 columns, so 2 x 3 = 6 detectors. Each detector sits 15 ft from the walls, which is half the spacing and within the allowed distance.
More questions: Submittal Preparation and System Layout
- 3010A corridor is 10 ft wide. Using the 0.7S rule with S = 30 ft (every point within 21 ft of a detector), what is the maximum spacing between detectors along the centerline?
- 3011A heat detector listed for 50 ft spacing is planned for a 20 ft ceiling. The multiplier for 20 ft is 0.64. What spacing applies?
- 3012A room is 40 ft by 64 ft with a 20 ft smooth ceiling. Heat detectors are listed for 50 ft (adjusted spacing 32 ft). What is the minimum detector count on a square grid?
- 3013A projected beam detector is listed for a maximum beam length of 330 ft and a width of 60 ft. How far from the side wall may the beam be placed?
- 3014A 20 ft by 30 ft room has a 10 ft ceiling and will use one wall mounted strobe in the middle of the long wall. Which room size must be used to pick the candela?
- 3015A room is 30 ft by 30 ft with one wall mounted strobe. What minimum effective intensity applies?