Which sheet item helps the reviewer confirm each wall mounted strobe will cover its room?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3005
- B: The candela rating shown next to each strobe
Explanation
Shop drawings mark each visible appliance with its candela setting so the reviewer can compare it with the room size tables. Speaker taps and horn settings are shown in the same way.
More questions: Submittal Preparation and System Layout
- 3006What must record drawings show at the end of a project?
- 3007Before laying out devices in an existing building, what is the purpose of a site survey?
- 3008Which ceiling condition found during a site survey changes smoke detector spacing?
- 3009A smooth ceiling room is 60 ft by 90 ft. Detectors are laid out on a 30 ft grid. How many spot smoke detectors are needed?
- 3010A corridor is 10 ft wide. Using the 0.7S rule with S = 30 ft (every point within 21 ft of a detector), what is the maximum spacing between detectors along the centerline?
- 3011A heat detector listed for 50 ft spacing is planned for a 20 ft ceiling. The multiplier for 20 ft is 0.64. What spacing applies?