Under the IBC, how must smoke alarms in a dwelling unit with more than one alarm be connected?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3038
- A: Interconnected so all sound when one activates
Explanation
Where more than one smoke alarm is required in a dwelling unit, they must be interconnected so that activation of one sounds all alarms in that unit. They normally do not activate the building wide notification system.
More questions: Submittal Preparation and System Layout
- 3039Under the IBC, which feature is required in high rise buildings for occupant notification?
- 3040Which section of NFPA 101 contains the general requirements for fire detection, alarm, and communication systems?
- 3041A 500 ft long corridor has an exit at each end. Manual boxes are placed within 5 ft of each exit. How many manual boxes are needed at minimum on that floor to meet the 200 ft travel distance?
- 3042A floor has four exit stairs and the travel distance to the nearest of them is always under 150 ft. How many manual boxes are needed on that floor?
- 3043A room is 45 ft by 75 ft with a smooth 10 ft ceiling. Using 30 ft spacing for spot smoke detectors, what is the minimum count on a regular grid?
- 3044A heat detector listed for 30 ft spacing is installed on a 15 ft smooth ceiling. The multiplier for that height is 0.77. What is the adjusted spacing?