Question 3043 of 344 · NICET Fire Alarm Systems Level II

A room is 45 ft by 75 ft with a smooth 10 ft ceiling. Using 30 ft spacing for spot smoke detectors, what is the minimum count on a regular grid?

Exactly one answer is correct.

Show solution

Correct answer to question 3043

  • B: 6

Explanation

45 / 30 = 1.5, round up to 2 rows. 75 / 30 = 2.5, round up to 3 columns. 2 x 3 = 6 detectors, with spacing reduced to about 22.5 ft by 25 ft.

Next to question ›