Question 3041 of 344 · NICET Fire Alarm Systems Level II
A 500 ft long corridor has an exit at each end. Manual boxes are placed within 5 ft of each exit. How many manual boxes are needed at minimum on that floor to meet the 200 ft travel distance?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3041
- A: 3
Explanation
With boxes only at the ends, the midpoint is 250 ft from either box, which exceeds 200 ft. Adding one box near the middle keeps every point within 200 ft, so 3 boxes are needed.
More questions: Submittal Preparation and System Layout
- 3042A floor has four exit stairs and the travel distance to the nearest of them is always under 150 ft. How many manual boxes are needed on that floor?
- 3043A room is 45 ft by 75 ft with a smooth 10 ft ceiling. Using 30 ft spacing for spot smoke detectors, what is the minimum count on a regular grid?
- 3044A heat detector listed for 30 ft spacing is installed on a 15 ft smooth ceiling. The multiplier for that height is 0.77. What is the adjusted spacing?
- 3045On a 12 ft ceiling, beams are 8 in. deep. How are the beams treated for spot smoke detector spacing?
- 3046Under NFPA 90A, an air handler has a supply capacity of 18,000 cfm. Where is a duct smoke detector needed on the supply side?
- 3047A design uses 18 strobes at 0.12 A and 10 horns at 0.03 A on one NAC. What is the alarm current?