Question 3037 of 344 · NICET Fire Alarm Systems Level II
Under the IBC, a duct smoke detector connected to a building fire alarm system activates. What signal is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3037
- A: A supervisory signal at a constantly attended location
Explanation
Duct smoke detectors connected to the fire alarm system must initiate a visible and audible supervisory signal and perform their fan control function. They are not meant to cause general evacuation, because they can respond to smoke from outside the building.
More questions: Submittal Preparation and System Layout
- 3038Under the IBC, how must smoke alarms in a dwelling unit with more than one alarm be connected?
- 3039Under the IBC, which feature is required in high rise buildings for occupant notification?
- 3040Which section of NFPA 101 contains the general requirements for fire detection, alarm, and communication systems?
- 3041A 500 ft long corridor has an exit at each end. Manual boxes are placed within 5 ft of each exit. How many manual boxes are needed at minimum on that floor to meet the 200 ft travel distance?
- 3042A floor has four exit stairs and the travel distance to the nearest of them is always under 150 ft. How many manual boxes are needed on that floor?
- 3043A room is 45 ft by 75 ft with a smooth 10 ft ceiling. Using 30 ft spacing for spot smoke detectors, what is the minimum count on a regular grid?