Question 3045 of 344 · NICET Fire Alarm Systems Level II

On a 12 ft ceiling, beams are 8 in. deep. How are the beams treated for spot smoke detector spacing?

Exactly one answer is correct.

Show solution

Correct answer to question 3045

  • A: As a smooth ceiling

Explanation

Beams that are less than 10 percent of the ceiling height are treated as smooth ceiling for smoke detector spacing. 10 percent of 144 in. is 14.4 in., and 8 in. is less than that.