Question 3046 of 344 · NICET Fire Alarm Systems Level II

Under NFPA 90A, an air handler has a supply capacity of 18,000 cfm. Where is a duct smoke detector needed on the supply side?

Exactly one answer is correct.

Show solution

Correct answer to question 3046

  • D: Downstream of the air filters, ahead of any branch

Explanation

Systems over 2,000 cfm need a supply side detector downstream of the filters and ahead of any branch connection. Systems over 15,000 cfm also need return side detection at each story served by a common return.

Next to question ›