Question 3046 of 344 · NICET Fire Alarm Systems Level II
Under NFPA 90A, an air handler has a supply capacity of 18,000 cfm. Where is a duct smoke detector needed on the supply side?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3046
- D: Downstream of the air filters, ahead of any branch
Explanation
Systems over 2,000 cfm need a supply side detector downstream of the filters and ahead of any branch connection. Systems over 15,000 cfm also need return side detection at each story served by a common return.
More questions: Submittal Preparation and System Layout
- 3047A design uses 18 strobes at 0.12 A and 10 horns at 0.03 A on one NAC. What is the alarm current?
- 3048Why should NAC current calculations use the appliance current at the low end of its operating voltage range?
- 3049A booster power supply is rated 8.0 A total. Its NACs serve 7.2 A of alarm load. What percentage of its capacity is used?
- 3050A small system has a standby load of 0.18 A and an alarm load of 1.9 A. It needs 24 h standby and 5 min alarm, with the 1.25 aging correction factor applied. Which standard battery size is the smallest that works?
- 3051Since the 2022 edition, what minimum correction factor must NFPA 72 battery calculations apply to the calculated amp-hour capacity to allow for battery aging?
- 3052A NAC run is 200 ft one way using 16 AWG stranded copper (4.99 ohms per 1000 ft). The alarm load is 1.0 A at the end. What is the voltage drop?