Question 3049 of 344 · NICET Fire Alarm Systems Level II
A booster power supply is rated 8.0 A total. Its NACs serve 7.2 A of alarm load. What percentage of its capacity is used?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3049
- D: 90 percent
Explanation
Use = 7.2 / 8.0 = 0.90, or 90 percent. This is within the rating, although many designers keep a margin of about 20 percent for future additions.
More questions: Submittal Preparation and System Layout
- 3050A small system has a standby load of 0.18 A and an alarm load of 1.9 A. It needs 24 h standby and 5 min alarm, with the 1.25 aging correction factor applied. Which standard battery size is the smallest that works?
- 3051Since the 2022 edition, what minimum correction factor must NFPA 72 battery calculations apply to the calculated amp-hour capacity to allow for battery aging?
- 3052A NAC run is 200 ft one way using 16 AWG stranded copper (4.99 ohms per 1000 ft). The alarm load is 1.0 A at the end. What is the voltage drop?
- 3053A NAC must deliver 2.5 A at 400 ft one way, and the allowed drop is 3.4 V. Which is the smallest solid copper conductor that works? (12 AWG = 1.93, 10 AWG = 1.21 ohms per 1000 ft)
- 3054Why does treating the whole NAC load as if it were at the last appliance give a conservative voltage drop result?
- 3055A 25 V speaker circuit serves 32 speakers tapped at 1 W and 8 speakers tapped at 2 W. What total power does the amplifier need to supply?