Question 3051 of 344 · NICET Fire Alarm Systems Level II
Since the 2022 edition, what minimum correction factor must NFPA 72 battery calculations apply to the calculated amp-hour capacity to allow for battery aging?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3051
- D: 1.25
Explanation
The 2022 edition replaced the earlier fixed 20 percent safety margin (2019 and before) with a minimum aging correction factor of 1.25, so a calculated 10 Ah becomes 12.5 Ah. Lead-acid batteries fall to about 80 percent of rated capacity at end of life, and 1/0.80 = 1.25. The 2025 edition keeps the 1.25 factor.
More questions: Submittal Preparation and System Layout
- 3052A NAC run is 200 ft one way using 16 AWG stranded copper (4.99 ohms per 1000 ft). The alarm load is 1.0 A at the end. What is the voltage drop?
- 3053A NAC must deliver 2.5 A at 400 ft one way, and the allowed drop is 3.4 V. Which is the smallest solid copper conductor that works? (12 AWG = 1.93, 10 AWG = 1.21 ohms per 1000 ft)
- 3054Why does treating the whole NAC load as if it were at the last appliance give a conservative voltage drop result?
- 3055A 25 V speaker circuit serves 32 speakers tapped at 1 W and 8 speakers tapped at 2 W. What total power does the amplifier need to supply?
- 3056Average ambient sound in an office is 60 dBA. A horn produces 90 dBA at 10 ft. In public mode, would a person 80 ft away (free field) meet the required level?
- 3057Why should ambient sound levels be measured during the site survey of an existing building?