A design places a spot smoke detector 2 ft from a supply diffuser. What should the reviewer note?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3067
- B: Airflow may keep smoke from reaching it, so relocate it
Explanation
Detectors should be kept out of direct supply airflow, often about 3 ft from diffusers per manufacturer guidance. Airflow can dilute or divert smoke so the detector responds late.