Power-limited fire alarm cable must be run without raceway through a ceiling cavity that is used as a return air plenum. Which cable type is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1005
- B: FPLP
Explanation
Cable installed in a space used for environmental air must be the plenum rated type, FPLP, unless it is installed in a suitable raceway. FPLR is the riser type and FPL is the general purpose type; both have lower fire and smoke ratings. NPLF is a non-power-limited cable type.