Which description matches pathway survivability Level 3 in NFPA 72?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1008
- D: Level 2 protection plus a building fully protected by automatic sprinklers
Explanation
Level 3 requires the 2-hour protection options of Level 2 and, in addition, a building fully protected by automatic sprinklers. Level 1 is sprinkler protection plus metal raceway, and Level 0 has no survivability attributes. A frequent mix-up is assuming Level 3 means a 3-hour rating.