Your crew has run fire alarm cable through a 2-hour rated corridor wall. What must you confirm before the wall is closed up?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1007
- A: The opening is sealed with a listed firestop system that keeps the wall rating
Explanation
Openings around electrical penetrations through fire-resistance-rated walls, floors, and ceilings must be firestopped with approved methods so the rating is maintained. Article 760 makes this general NEC rule apply to fire alarm cable as well.