Your crew has run fire alarm cable through a 2-hour rated corridor wall. What must you confirm before the wall is closed up?

Exactly one answer is correct.

Show solution

Correct answer to question 1007

  • A: The opening is sealed with a listed firestop system that keeps the wall rating

Explanation

Openings around electrical penetrations through fire-resistance-rated walls, floors, and ceilings must be firestopped with approved methods so the rating is maintained. Article 760 makes this general NEC rule apply to fire alarm cable as well.